Went to carry out condition report on a flat. There is no earth cables from fuseboard to first point . The installation is over 30 years old and other contractors have just added twin and earth under floors/walls. R1+r2 values seem to be high aswel. Zs is not so bad and is within allowed time.main bonding to gas is 2.5 single earth and main earth from pyro cable is 6mm. The tenant and i could not find the main water supply to see if it was earthed. No isolators for equiptment in kitchen. Socket wired from cooker circuit in 2.5mm t&e on 32amp breaker. Cooker is wired in 6mmt&e.earths not connected at light switches and they are using metal plate switches.
i was goin to advise arewire wat are your thoughts?
Is the conduit allowed to be used as an earth or do you need a earth cable installed?
i was goin to advise arewire wat are your thoughts?
Is the conduit allowed to be used as an earth or do you need a earth cable installed?