A

aaelectric

Went to carry out condition report on a flat. There is no earth cables from fuseboard to first point . The installation is over 30 years old and other contractors have just added twin and earth under floors/walls. R1+r2 values seem to be high aswel. Zs is not so bad and is within allowed time.main bonding to gas is 2.5 single earth and main earth from pyro cable is 6mm. The tenant and i could not find the main water supply to see if it was earthed. No isolators for equiptment in kitchen. Socket wired from cooker circuit in 2.5mm t&e on 32amp breaker. Cooker is wired in 6mmt&e.earths not connected at light switches and they are using metal plate switches.
i was goin to advise arewire wat are your thoughts?
Is the conduit allowed to be used as an earth or do you need a earth cable installed?
 
Of course Metal conduit is allowed to be the CPC for whatever circuits are enclosed in the system. The only time you should need to include a separate CPC conductor in a well installed conduit system, is if and when the conduit is breaking down due to corrosion...

You obviously need to upgrade the bonding conductors to the service pipes!! Maybe also upgrade the flying lead off the MICC supply cable to a 10mm...

As for rewiring the system, that depends on the condition of the installed wiring?? The T&E wiring was probably installed for placement of extra/additional socket outlets etc, that the original conduit system didn't cover!!
 
As stated the r1&r2 value is very high and the conduit is behind walls cupboards etc. this leads me to think there is some corrosion on conduit.
what about isolators for appliances in kitchen, bathroom fan etc do they have to have isolators. Also the 2.5 comin off 6mm on a 32amp breaker
cheers for the advise
 

Reply to Using conduit as earth. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
900
In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
460

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top