atm84

-
Joined
Aug 7, 2011
Messages
834
Reaction score
94
I have recently come across a situation whereby instead of running a main equipotential bonding conductor from the MET to the incoming water someone had instead ran a short bond from the MET to some copper pipe in the mains cupboard and clamped it and then placed a bond on the pipe near the incoming water (at the other end of the property) and bonded to the incoming water there.

Wander lead method states 0.02 ohms resistance.

I know this is not good practice but where does it say in the regs it has to be a continuous conductor and that you can't do it.
 
regs. specify that the bond to an incoming service should be within 600mm of the point of entry to the building, or as close as practicable. the scenario you describe might be fine as it stands, but when wet-pants comes along and cuts out some copper andreplaces it with that crappy DIY plastic crap, then you've lost your bond to the extarneous incoming service.
 
Obviously not a good idea as Tel says.
GN8 says that if the bonding is looped between services (e.g. MET to gas then gas to water) the the conductor should remain unbroken.
However 543.2 says that a bonding conductor can be a variety of different materials (many of which would require numerous joints) but do specify that the continuity of the bonding should be assured.
 
This could also be one of the occasions,where a visual,physical examination,could provide a better indication of possible issues,as 1x PFC is not available on the MFT :cyclist:
 
Guys cheers for the comments. I agree not ideal but I explained the scenario about the plumber coming along and cutting the pipe and the connection being lost. The section in GN8 certainly does say about the connection being unbroken however this reads as more of a 'recommendation' than a 'requirement' and describes a slightly different scenario.

I would never do it myself, I think it's poor practice but at the moment there is a bond. The resistance meets regulations blah blah blah. Would anyone give it a code when carrying out EICR?
 
That's the bonding connection itself. Not the length of bonding cable. You can only work out what that should be by using the tables of resistance. Daz
 

Reply to Using pipe work to bond to incoming water in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
865
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
984

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top