P

paulsamuel1984

I am currently carrying out a design for a 4kW system, using class 2 modules, cables and connectors. using sunnyboy 3.8kW (with isolation transformer).

Having read the dti guide i am sure I am to leave this system floating (TNCS earthing system). i.e. I will not connect/bond the rails, frame etc, and will then not connect to new earth spike.

can someone confirm if this is the right thing to do?
 
Thanks for this. The reason I am second guessing myself is because I have been speaking to a fellow installer who bonds framing / mounting structure etc. together even though the array is left floating. so, in short everything is bonded together but there is no connection to either earth rod or met.

Am I missing something? there is no merit in carrying this process out unless you are connecting to earth. correct?
 
Earthing of the array is not required,also earthing for lightning protection is not required. you only have to earth the array if the inverter does not have an isolating transformer between AC and DC parts or any conductive part of the array and frame is in the equipotential zone.
 
Earthing of the array is not required,also earthing for lightning protection is not required. you only have to earth the array if the inverter does not have an isolating transformer between AC and DC parts or any conductive part of the array and frame is in the equipotential zone.

Why would you want to earth a class II installation or bond a non extraneous conductive part, even if it is within an equipotential zone?
 
How would these rails develop a fault, they are not exposed conductive parts because the panels are Class II equipment, and unless there is a chance of the rails being at a different potential and therfore a extraneous conductive part, which is highly unlikely on a floating rail, then earthing and bonding can be more dangerous, as you could transfer a fault from the equipotential zone onto the frame work.
 
Perhaps a fault on the cable? Perhaps from damage from vermin or birds?

I just think there is a special risk with PV in that the installation is hidden from view yet not shielded from damage. These systems are likely to be on a roof for a long time.

I'm not saying bonding the rails together is the right thing to do, I'm just asking other opinion.
 
Perhaps a fault on the cable? Perhaps from damage from vermin or birds?

I just think there is a special risk with PV in that the installation is hidden from view yet not shielded from damage. These systems are likely to be on a roof for a long time.

I'm not saying bonding the rails together is the right thing to do, I'm just asking other opinion.

Not sure if birds would attack it Briggs but I do see your point about vermin or squirrels. Is there in corelation between Panel double insulated tails and vermin attack.
 

Reply to usual question - pv array earthing! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
900
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
  • Sticky
Hi Richard, thanks for your comment. The relay is rated 12A peak. It's also worth noting that a relay contact will perform differently depending...
    • Like
    • Winner
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top