Then it is wrong. You are probably getting away with it whilst house consumption is more than pv generation, but as soon as the pv starts trying to push power the wrong way through the vphase then as it is not designed to work like that, the voltage rises and pv cuts out out, voltage falls, pv restarts, voltage rises, pv cuts out..........................................
 
Last edited:
Thanks for your time and explaining, the reason we had a voltage optimizer was because the incoming voltage was very high but within regs and this is why the company installed it, would like to say, that the quality of there work was **** poor!! thanks
 
A V phase only goes on dedicated curcuits too, sounds like they did not read the instructions.

Just get a sparky to disconnect the unit.
 
I am not generally a fan of VOs, but your situation might still be a good reason for you to have one. But the pv must be connected the other side of it. If you are working G83 rather than G59 then your inverter does not have to cut out until it gets to 264V, so you should still have a good margin for it to work. You need an installer who knows what they are doing.
 
Just out of interest, and this is not a dig, but what made you choose this company to do your install?
 
Thanks again, the reason my dad choose the company was that we knew people who had installed and all was ok. just want to stress on one point, ill remove the voltage optimer but the vac problem still there, how can there mend this problem, just want to stress that i will not be doing anything with the solar equipment because im not qualified and haven't done work in this field
thanks
 
What is the normal supply voltage without the PV running?
When the system is running check the voltage again at supply, and also at the inverter.

This could show you whether you have an install or supply voltage problem, there is also the possibility that the inverters have not been set to UK spec.

You can contact the DNO and ask them to turn down the voltage, however you need to check that your house is in order first.

This does have a risk though, if their system is within tolerance (216V-253V) and your PV system is pushing it over they can order you to shut your system off, even if you have the correct approval from them to install in the first place.
 
The installer's worlmanship warranty should cover this - insist that they come out and sort it.

In addition workmanship is covered under their scheme they are registered with - so if you still don't get satisfaction a call to Elecsa / Napit / NICEIC etc or however they are registered with may kick them into action...

Voltage Drop is also probably one of your issues, a 4kWp systems south facing with giood quality inverter with 80m run from inverter to DB would need a 25mm2 SWA cable just to cope with the allowed 1% voltager drop, the 100m run will also need 25mm2, - what size did they install?

(We work on 20m max 6mm2, 35m max for 10mm2, and 65m max for 16mm2)
Cable sizing
The grid impedance of the AC cable must not exceed 1 ohm. Otherwise, the inverter will disconnect at full feed capacity due to excessive voltage at the feed-in point.

The conductor cross-section should be dimensioned such that cable losses do not exceed 1% at nominal power

The conductor cross-section required in individual cases depends on the following factors, among others:
• Ambient temperature,
• Routing method,
• Cable losses,
• Valid installation requirements of the respective country (installation location)

(PV systems only allow 1% not 3% or 5% VD to cope with the way inverters monitor and power the grid)

If the installer won't sort it (which they should foc - part of their warranty on workmanship), then as you're in Gloucestershire, someone like BruceB or ourselves could come out and sort it out for you on a paid for basis and then take the installer to the small claims court to sort it. (I'm not pitching for the work by the way :) )
 
The installer's worlmanship warranty should cover this - insist that they come out and sort it.

In addition workmanship is covered under their scheme they are registered with - so if you still don't get satisfaction a call to Elecsa / Napit / NICEIC etc or however they are registered with may kick them into action...
None of the above will be interested. All they do is pass the problem on to each other, and you end up going round in circles.:cuss:
 
I'm NOT suggesting he goes down the Gemserve / RECC (nee Real) route that is a waste of time. Workamnship quality should be of interest to their electrical certifying body though.
 
Be great if we could see some pics, it might not be too bad, there again it might be.

Any pics Dave992?
 