Hi again..
Did a Ze reading and almost fell over as the result was 600+ ohms.
I thought I was testing a TCNS system but now I am lost.
There are no rcd's in the entire installation so I cant see it being TT?
The pics show the head with the provided earth henely block
and the supply cable with the 16mm earth lead taped onto it exiting the building.
The cables head into the soil and thats the last I can trace them.
I cannot find an earth rod anywhere??
is this a new TNCS supply installed and never had the earth changed?
any ideas greatly appreciated???
 

Attachments

  • [ElectriciansForums.net] Very high Ze ...no rcd?
    earth exit.jpg
    67.1 KB · Views: 72
  • [ElectriciansForums.net] Very high Ze ...no rcd?
    head.jpg
    64.6 KB · Views: 72
  • [ElectriciansForums.net] Very high Ze ...no rcd?
    earth.jpg
    62.2 KB · Views: 74
I would say it looks like a TN-S system.
Is that an earth cable from the bottom of the earth block going to the incoming supply cable ??

If it is TN-S, then call supplier as there maybe a fault at their end.
Best regards,
Sav
 
i am glowing from all the stinging nettle!!
Why do you think its TT when there is no 100mA RCD before any CU?
cheers
 
I would say it looks like a TN-S system.
Is that an earth cable from the bottom of the earth block going to the incoming supply cable ??

If it is TN-S, then call supplier as there maybe a fault at their end.
Best regards,
Sav

The supply looks like a typical thin tncs supply. the bottom earth cable is not attached to the supply cable armouring like a typical tns that I know. it just runs alongside it into the soil.. But yes thats the earth supply and I dont know where it comes from?
 
It maybe then a TT supply and somehow the earth cable has become dislodged or snapped off from the rod due to exposure / old age etc .

Are the homes next door TT suply ?? Can you look, just to verify ??

Sav
 
Hi again..
Did a Ze reading and almost fell over as the result was 600+ ohms.
I thought I was testing a TCNS system but now I am lost.
There are no rcd's in the entire installation so I cant see it being TT?
The pics show the head with the provided earth henely block
and the supply cable with the 16mm earth lead taped onto it exiting the building.
The cables head into the soil and thats the last I can trace them.
I cannot find an earth rod anywhere??
is this a new TNCS supply installed and never had the earth changed?
any ideas greatly appreciated???


This is a tn-s service, at some stage the service has been altered, the supply cable is 2 core used for tn-c-s, the seperate 16mm earth is to maintain the tn-s status, this is common practice in service alterations or replacament of lead sheath services after faults, the dno has the reposibility to to repair the earth, no doubt they wiill suggest a change to pme if the installation permits
 
I had similar probs in my house. DNO were great and repaired same day. Also upgraded 60A ---> 100A FOC and fitted contractors isolator :)
 

Reply to Very high Ze ...no rcd? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top