Did an EICR today, Ze was 500ohms!

Went through the whole process though.

There is an up front time delayed 100mA RCD and a 30ma RCD protecting the sockets - 16th Edition board.

100mA trips ok at x 1

30mA trips ok at x1 but not at x5. It does trip at 100mA.

Could it be that the very high Zs causes the 30mA RCD failing to trip at x5?

Obscure make of CU (and RCD) so if this is the cause of the RCD failing then hopefully I won't have to change the RCD if the Zs was more appropriate.
 
Did an EICR today, Ze was 500ohms!

Went through the whole process though.

There is an up front time delayed 100mA RCD and a 30ma RCD protecting the sockets - 16th Edition board.

100mA trips ok at x 1

30mA trips ok at x1 but not at x5. It does trip at 100mA.

Could it be that the very high Zs causes the 30mA RCD failing to trip at x5?

Obscure make of CU (and RCD) so if this is the cause of the RCD failing then hopefully I won't have to change the RCD if the Zs was more appropriate.


A 30ma RCD should trip at much higher Zs readings than 500 ohms....so no.
Test at RCD with nothing connected to the load side if you are not already.
 
Have you tried it against the incoming neutral? Just to see?

Sorry don't understand what you'e getting at.

If you're implying that I could have PME, then thats possible. There is a label on the meter board that specifically says no PME, but the overheads have been renewed recently and a solution could be to call SSE in to check if PME is now possible. New overheads means there is more earthing along the route, from what I was told it used to be every 4th pole now its every other pole.

- - - Updated - - -

C1 or C2 then!

Not sure what Cat I'm giving it yet, but definately unsatisfactory!
 
the RCD should trip on test irrespective of the Ze, even if there's no earth at all. you are confusing the 1667 ohms with fault protection. i would suggest replacing the RCD and , as you say, investigating earthing.
 
If you have a Ze of 500 ohms then the fault current would be 230/500 = 0.46 A = 460 mA so there is enough current flow to allow the 150mA current you are applying to test at x5.

If the RCD trips at 100mA and not at 150mA this is strange, I assume you tried a couple of times so it was not just a poor connection at the probe.

If you tested the RCD: load Line to supply neutral, this should have the same effect as testing to earth and would ensure the problem is not the Ze.

Either way it sounds initially like a shot RCD, sorry.
 
Sorry don't understand what you'e getting at.

If you're implying that I could have PME, then thats possible. There is a label on the meter board that specifically says no PME, but the overheads have been renewed recently and a solution could be to call SSE in to check if PME is now possible. New overheads means there is more earthing along the route, from what I was told it used to be every 4th pole now its every other pole.

- - - Updated - - -



Not sure what Cat I'm giving it yet, but definately unsatisfactory!
its a 2....dangerous under fault condidions
 
With a Ra of 500 ohms, it's at least a code 2, before you even get to the RCD side of things!! At least this TT system has a 100mA S type back-up facility!! So at least 2 code 2's before you get past the CU!! lol!!

Think it would be prudent to enquire about the possibility of a PME connection. I'd still replace the existing Rod with a new 2 X 5/8'' rod position giving the installation a local N-E connection (via the MET). But at the moment, your only conducting a EICR. As far as i am aware, it's still every 3rd pole that an overhead supply has a N-E connection made on a PME'd O/H system.
 

Reply to Very High Zs and RCD not tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top