Did an EICR today, Ze was 500ohms!
Went through the whole process though.
There is an up front time delayed 100mA RCD and a 30ma RCD protecting the sockets - 16th Edition board.
100mA trips ok at x 1
30mA trips ok at x1 but not at x5. It does trip at 100mA.
Could it be that the very high Zs causes the 30mA RCD failing to trip at x5?
Obscure make of CU (and RCD) so if this is the cause of the RCD failing then hopefully I won't have to change the RCD if the Zs was more appropriate.