hi everyone, but stuck at the mo with a zs of 6.49ohms. simple job of fitting spur to existing ring. all other sockets on the ring are also 6.49 ohms. the normal ring health checks are good with ratios maintained throughout. initial thought was poor distributor earth. ze checked out at 150 ohms, badly corroded and tarnished MET and distributor earth cable. after cleaning, ze (all earths disconnected) 0.12. reconnected earths and checked ze from the consumer unit earthing block and the MET. both reading 6.49 tried disconnecting main bonding conductors, no effect. tried disconnecting circuit earths one at a time, no effect.
supply is TNCS, and the c/u and meter are in a very damp cellar. the ring i have worked on is protected by rcd so is quite safe using the 1667 reg but there are other non rcd protected circuits, so i am not happy leaving it like this.
in short, the ze is ok untill the consumer unit earth is connected to it then it increases to 6.49
any ideas
supply is TNCS, and the c/u and meter are in a very damp cellar. the ring i have worked on is protected by rcd so is quite safe using the 1667 reg but there are other non rcd protected circuits, so i am not happy leaving it like this.
in short, the ze is ok untill the consumer unit earth is connected to it then it increases to 6.49
any ideas