hi everyone, but stuck at the mo with a zs of 6.49ohms. simple job of fitting spur to existing ring. all other sockets on the ring are also 6.49 ohms. the normal ring health checks are good with ratios maintained throughout. initial thought was poor distributor earth. ze checked out at 150 ohms, badly corroded and tarnished MET and distributor earth cable. after cleaning, ze (all earths disconnected) 0.12. reconnected earths and checked ze from the consumer unit earthing block and the MET. both reading 6.49 tried disconnecting main bonding conductors, no effect. tried disconnecting circuit earths one at a time, no effect.
supply is TNCS, and the c/u and meter are in a very damp cellar. the ring i have worked on is protected by rcd so is quite safe using the 1667 reg but there are other non rcd protected circuits, so i am not happy leaving it like this.
in short, the ze is ok untill the consumer unit earth is connected to it then it increases to 6.49
any ideas
 
Not quite sure i have fully followed what the changes and readings were, however if your Ze of 0.12 ohms was from the main earthing conductor directly (standard test method) and then you were later measuring Ze from the MET and then from the CU earth bar and both Zes were 6.49ohms even after cleaning then I would say that you have a problem with the MET being dirty inside the terminals and not providing a low resistance connection to the CU.
If you change the MET block and, if required, the earth cable from MET to CU you may find the Ze is now OK.


For the socket circuit:
If you were measuring Zs also at 6.49 ohms for the socket circuit then this is odd as the socket circuit has zero resistance, so by calculation what would be your R1+R2 +Ze?

If this is within limits then you have reduced the high resistance joint to being MCB, RCD, Main switch, earthing conductor, MET.
since this includes the MET and earthing conductor likely to be the culprit.
 
apolgies for delay, new met fitted, new main earthing conductor fitted, distributor earth cable cleaned on every strand, everything now fine. all down to corrosion.
 

Reply to very high zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
386
Yes, probably overthinkig, thanks.
Replies
6
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top