Being looking at sizing Cable for a new Cooker . It is a Beast with a manufacturesrs spec of 17.4 KW. Was applying diversity to this ie 10amps plus 30% etc ( no 5 amp).
Just got me thinking that after the diversity the answer is 29.7 Amps down from 75.6amps. Was diversity designed to allow for large cookers or are the regs need updating as manufactures build even bigger appliances.
Does Diversity of 30% work on such Large Cookers and what happens when the Client has all the rings and Oven on ( eg Xmas Lunch their words not mine).
I am adding in the 5 amps ( though not using socket outlet) to get Cable and Protection size and definitly 10mm cable