So, I unplugged an extension lead from the problem socket (which had been switched off at the socket anyway) and tested again, and it's back to > 299 Meg. Very odd - socket should have isolated any fault with any connected stuff.

.

5-W-W
A possible reason could be that the sockets are single pole and a low insulation reading on the extension cable was being picked up via the neutral of the socket, then clear again when it was unplugged
 
low resistance N-E perhaps ?? these aren't isolated at the S/O

and a Resistance of three hundred and ten thousand ohms (o.31 meg) wouldn't pull enough current to trip an RCD

would be looking at about 0.0007A ?
 
i have had low results before (other than forgetting to unplug appliances) it was the actual socket /spur/switch itself that was the problem. to make sure you could put cables into connectors and retest. if there has been decorators or plasterers you can bet they are to blame.
 
Just installed a max ring, (100 meters) loads sockets but very low max demand, and on doing R1+R2 at the sockets found that one side of a socket was reading 1.0, the other 0.41. o.41 being the expected. One of the phase wires was badly connected in that half of the DSSO. This would of caused havock when testing ir later.So being inexperienced on falt finding ( getting better and better ) I consider that day to be a good onefor experience on DSSO's.
 
Just installed a max ring, (100 meters) loads sockets but very low max demand, and on doing R1+R2 at the sockets found that one side of a socket was reading 1.0, the other 0.41. o.41 being the expected. One of the phase wires was badly connected in that half of the DSSO. This would of caused havock when testing ir later.So being inexperienced on falt finding ( getting better and better ) I consider that day to be a good onefor experience on DSSO's.


What is DSSO's ????
 

Reply to Very low insulation resistance on ring? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
605
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
377
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top