hi all hoprfully someone here can answer this question for me: i tested a sub mains today and i only got 0.35 KA is this normal for a submains as at the main mainsboard the pfc is 3.3 KA the main fuseboard has a rcd main switch so at the submain i had to use no trip pfc not sure is this makes and difference any imput would be great.
regards
 
Hi Lucus

What was your Zs at the sub main ? It will be higher than at the origin so therfore the PFC will be lower.

So as long as all protective devices throughout the installation have a breaking capacity equal to or more than the origin main protective device,then recording the origin PFC is good enough.

Mark
 
That PFC would be for a Zs at the board at around 0.65 ohms. So not sure where you're going wrong there.... You should be getting a PFC of around 0.68kA if all correct.
 

Reply to very low pfc on submain board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K
Good one . Thanks. I was finding Fluke etc ÂŁÂŁÂŁ!
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top