Very low reading of PFC test | on ElectriciansForums

Discuss Very low reading of PFC test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

dhaval

hi,
I did Ze test, I got 0.22 ohms but PFC test I got 22 Amps. it is very low. I am expecting a (230/0.22=1045 amp ) by theory
So pls let me why it is very low reading
 
I'd try the test again as somethings not quite right. Did the earth lead from the test instrument have a good connection? Also did you try testing to neutral as this should give a higher perspective fault current than to earth? (unless if it's tn-c-s where they should be more or less the same value as the neutral and earth are linked in the service head).

Let us know how you get on.
 
Why? I've had loads of sub 1 ohm readings on TTs.

I bet they wern't fitted within the last 10 years! Are we going to get to here about your one in the middle of the house again Trev! :wink:
 
No, I was just making a point mate. It takes a bit of work but it can be done.
Oh, and some of them were done in the last ten years

I was only pulling your leg Trev :smiley2:
 

Reply to Very low reading of PFC test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I have known some inverters to be damaged by insulation testing. as a general rule, i tend to avoid doing an insulation resistance test on things...
Replies
8
Views
231

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top