I might be overlooking something that's right under my nose but opinions would be much appreciated. I visited a customer today with a detached garage supplied with power from a 13a RCD fused spur in the conservatory [spurred off RFC].
The RCD is 'tripping' randomly so I went to investigate.
The unit in question must be around 15 years old or more and immediately I found that the test button did nothing, a test at a garage socket also failed at x1 and x5 and the RCD refused to operate and I then found the same with the load disconnected testing at the spur itself. [SFCU in case of pedantry:)].
So after isolating and doing an insulation resistance test at 250v with everything switched on in the garage [freezer and lights] which showed around 40 Megohms L-E & N-E I fitted a brand new BG Nexus RCD SFCU, upon powering up the test button worked perfectly but in the garage both my tester and Kewtech plug in socket tester are showing L-E reversed ! :eek:
With the supply and load cables connected together everything is fine [Highest Zs is 0.79 at the furthest garage socket].
So I have another replacement unit to fit tomorrow, it has to be that, right ?
I can't think of anything else which could cause this but opinions are most welcome even if I'm being dumb. :)
Sorry about the long winded tale !
 
Hi - I was just going to suggest to check through the installation earthing. Perhaps a wander lead from met to that outlet so it's 100% that earth is where it's supposed to be :)

Thanks Wilko, yes I'm certain about that, with the new spur in place the garage lights wouldn't come on either. I'm 99% certain it's a dodgy unit but doubts creep in as it's brand new and I can't see how the internal circuitry could create this. But if I'm right it's a very dangerous RCD. :eek:
 
with the RCD out of circuit, then test for polarity. if it's right then then it is a duff RCD. dangerous and should be brought to manufacturers attention in case they have made a faulty batch.
 
with the RCD out of circuit, then test for polarity. if it's right then then it is a duff RCD. dangerous and should be brought to manufacturers attention in case they have made a faulty batch.

That's exactly what I did Tel, I know it has to be the RCD but it just seems so odd. I have another to fit in the morning so will update tomorrow, thanks.
 

Reply to Very odd problem what do you think ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
974
  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top