Hello all, I'm new to this but seeking some advice.
Just done an eicr, all lighting is white 1980s cabling, as is MOST of the power cabling. However, there are random 2-
3 sockets in old vir wiring, this is generally a no no to deal with, however, the consumer needs upgrading. Can I do this and sign off knowing that vir cabling is within the installation ??
Any advice is appreciated
 
Have you done any IR testing? If so what are the results? It’s well past its service life
If it's not taken much, load wise, and is undisturbed, it could be in good enough condition. The problems occur, because of age, with heavy use.
Problems could occur if disturbing, even for testing, especially at connection points.
 
If it's not taken much, load wise, and is undisturbed, it could be in good enough condition. The problems occur, because of age, with heavy use.
Problems could occur if
Strangely I have a 3 metre length under my stairs from when the house was rewired (buckle clips were too good quality to remove) and it’s in perfect condition. Other end of the same cable was completely falling apart.
 
As above, the simple act of pulling an old CU over it and feeding it into a new one and forming it to where it needs to go can finish it off.
If it IR tests ok then you may get away with carefully feeding a new CU over it and wago’ing pvc onto it for final connection. I’ve done this a couple of times in circumstances where an immediate rewire wasn’t possible.
 
As above, the simple act of pulling an old CU over it and feeding it into a new one and forming it to where it needs to go can finish it off.
If it IR tests ok then you may get away with carefully feeding a new CU over it and wago’ing pvc onto it for final connection. I’ve done this a couple of times in circumstances where an immediate rewire wasn’t possible.
Thankyou all for the comments. I don't think I was too clear - there is NO vir cables at the fuseboard, just white twin and earths, continuity tests out ok, didn't do an IR test in all honesty, the vir cables are just at a couple of sockets, no idea where they go or what they connect into. I did get a good earth loop reading on the vir sockets
 
Friendly advice, before you start at least do a global IR L+N together to CPC bar at 250v.

Without it you have no idea if things are safe.
Also if adding RcD protection you want to know that earth leakage is within tolerable limits.
Thankyou for the advice and will take that on board moving forward. There is currently an rcd main switch which trips within required times, so no issue there. The circuits are doubled up and I need to re run a 6mm for cooker so upgrading the board was the best option. It's just this vir in a socket that concerns me, as by changing the board, you re signing off the install
 
Friendly advice, before you start at least do a global IR L+N together to CPC bar at 250v.
Definitely good advice!

250V means it should not complain about any surge protection built in to stuff that is still connected, and if you get a sensibly good global value you have far less to worry about.

Of course if it fails you do have an issue, but sometimes that is down to an RCD socket outlet or similar (that was designed to trip on open-neutral or reverse polarity fault, so it has a sense resistor to E).
 
Thankyou for the advice and will take that on board moving forward. There is currently an rcd main switch which trips within required times, so no issue there. The circuits are doubled up and I need to re run a 6mm for cooker so upgrading the board was the best option. It's just this vir in a socket that concerns me, as by changing the board, you re signing off the install
But what are your IR results on this VIR cable? That’s really the main issue, you can’t sign anything off unless you have done your testing.
 
Don't put all your faith in an IR test. You need to thoroughly inspect the cable and it's terminations before deciding whether or not to proceed with this.

That cable has well exceeded it's service life and you should really be looking at options to replace it.

As it is VIR it will be using the steel conduit as the CPC so you also need to thoroughly inspect and test that.
 
Don't put all your faith in an IR test. You need to thoroughly inspect the cable and it's terminations before deciding whether or not to proceed with this.
I'd contend that any visual inspection would need to cover 100% of the cable.

I've seen rubber cable that has been perfectly supple and in excellent condition along the majority of its length, but with very small sections crumbling. In the OP's shoes I'd be absolutely certain about where I stood, before signing this off.
 
There’s also a commercial aspect to this too - assuming that it visually looks OK and you get an IR above 2Mohms, technically you’re OK to proceed however the client is going to be less than impressed when it fails in a years time and Sparky No.2 is giving you a right bashing for not having changed it ‘when it made sense’. I’d talk to the client and explain the overall situation and best practice would be to replace it regardless of if it still works today or not.
 

Reply to Vir cabling allowed for fuseboard change ?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
Thank you for fast response. The reason I asked is because I had read elsewhere online: "Electric ovens have a wattage rating that tells you how...
Replies
2
Views
2K
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top