A

adam.h

I have a run of garden lights to wire up, roughly 1000w so about 4.3A. If they are on an rcd spur from the ring main, is the volt drop allowed for a lighting circuit (3ish %) or for ring main (7% is it)? As 100m at 4.3A will require 4mm if my calcs are correct for a 3% Vd.
 
Adam, The allowed voltage drop is a maximum of 3% for lighting and 5% for other uses, when supplied directly from a public low voltage distribution system. For every metre your cable run exceeds 100m you may increase the voltage drop by 0.005% /metre up to a maximum of 0.5%. You may also apply diversity to your garden lights at 66% of total current demand. The voltage drop can be calculated from the current demand of the lights having applied diversity, or from the design current of the circuit as appropriate. Remember to calculate the maximum voltage drop for the whole final circuit and NOT just the spur.
 
Last edited by a moderator:
I have a run of garden lights to wire up, roughly 1000w so about 4.3A. If they are on an rcd spur from the ring main, is the volt drop allowed for a lighting circuit (3ish %) or for ring main (7% is it)? As 100m at 4.3A will require 4mm if my calcs are correct for a 3% Vd.

Your voltage drop should be calculated from the origin of the supply to the end of the circuit.

As you are spurring off a ring circuit then the voltage drop of the ring circuit must be taken into consideration.

So the sum of the voltage drop of the ring circuit and the voltage drop of your lighting circuit needs to be 3% max.

Hope that helps.
 
You may also apply diversity to your garden lights at 66% of total current demand.

As these are garden lights I presume they would all be on together, so you shouldn't apply any diversity.

And as Jud says, you should take the load of the circuit you are spuring off into account.
 
Yes, they would all come on at the same time so diversity would not be taken into account. I just got to check that the nearest socket is not a spur itself!

If the lights were wired up in a ring configuration (as they will be going all around the garden anyway) theroatically this would reduce the Vd, would you work out the Vd then with half the length (so 50m instead of 100m) or best to keep the lights wired in a series / radial configuration, so to speak.
 
Then the supply would need to be either split to a separate cu or a cu change. Which I don't mind doing :p but they won't lol


Still think i would go with something like a shower CU not going to be much different in price to a rcd fcu.



If you go for the radial spur option then the volt drop calc is a whole series of calcs up to the individual lighting points as the current at each point will decrease. So full current up to first point, then the short section up to the next point with slightly smaller current and so on. Vd on individual sections then added up to give total Vd.
The Vd on the ring then also has to be considered and this is even more complex as it would depend on the load on that circuit and its length.


As 100m at 4.3A will require 4mm if my calcs are correct for a 3% Vd
.

Not a single calc, as said above, as by the time you get to the end of the circuit there will not be 4.3 A
 
Last edited by a moderator:
Yea I had completely forgot about that. It was late though :p

Going to separate the supply as suggested as they are also thinking about having a work shop at the end of the garden.
 

Reply to Volt drop on spurred lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N
hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
327

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top