Looking to supply power to two outbuilding/sheds to be used as offices (no electric heating required). one is 60m from supply source and another is 10m further on.
I'm currently debating what size supply / cable to install taking volt drop into account.
Ideally in unit 1 i'd have
-16a radial socket circuit
- 6a lighting circuit (1.3A Ib)
- 16a circuit to supply unit 2 sockets and fcu for lighting
Any ideas on what the best way would be to do this???? The volt drop gets a bit wild on a run this length.
To work out the total volt drop, would i first work out the volt drop on the swa run to the 1st unit (60m) using full design current for both units 26.3A then add the volt drop of the second leg (10m) using the Ib of the 2nd unit (12.6A) then add the volt drop for the furthest lighting point in unit 2. Then add them all together and make sure it's less than 3% 6.9v. Is this right?
Does my design current sound a bit high? each unit is having 3 sockets and 3 lights. Sockets are for basic office stationary and domestic appliences only.
I've calculated it using 90% of lighting (2.3A)
100% of 1st socket circuit (16A)
50% of 2nd socket circuit. (8A)
26.3A
=====
Looking to supply power to two outbuilding/sheds to be used as offices (no electric heating required). one is 60m from supply source and another is 10m further on.
I'm currently debating what size supply / cable to install taking volt drop into account.
Ideally in unit 1 i'd have
-16a radial socket circuit
- 6a lighting circuit (1.3A Ib)
- 16a circuit to supply unit 2 sockets and fcu for lighting
Any ideas on what the best way would be to do this???? The volt drop gets a bit wild on a run this length.
To work out the total volt drop, would i first work out the volt drop on the swa run to the 1st unit (60m) using full design current for both units 26.3A then add the volt drop of the second leg (10m) using the Ib of the 2nd unit (12.6A) then add the volt drop for the furthest lighting point in unit 2. Then add them all together and make sure it's less than 3% 6.9v. Is this right?
Does my design current sound a bit high? each unit is having 3 sockets and 3 lights. Sockets are for basic office stationary and domestic appliences only.
I've calculated it using 90% of lighting (2.3A)
100% of 1st socket circuit (16A)
50% of 2nd socket circuit. (8A)
26.3A
=====