zone77

-
Joined
May 13, 2009
Messages
59
Reaction score
0
Location
Barrow
When doing a volt drop calc for a sub board, is the max volt drop 5%(11.5v) ( the sub board feeds lighting and power circuits) or is it reduced to 3% (6.9v):confused:
 
Does it not matter if its for public or commercial use, or am I confused?.

Just looked in BRB and it says

Public lighting 3% other 5%

Private 6% other 8%

Ah and just reading your post agian I see your point I would go with 5%.
 
Last edited by a moderator:
If the sub-main is feeding lighting circuits, the the max VD from the origin to the end of the lighting circuit fed from the sub-main DB is 3%.
 
VD is calculated from the origin of an installation in this case the house so you must include the sub-main as part of the lighting circuit.


This is from the ECA.....

Answer by the ECA: The overall voltage drop limit is 3% (6.9V) single-phase, if the sub-main is feeding lighting circuits.
 
Zone 77 it dosnt matter where it is. f its from the public supply thw max volt drop from Origin is
lighting 3%
power 5%

When its designed you will find distribution cables may be oversizes so less volt drop so it can be allowed for on the final circuits.
 

Reply to volt drop query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
676
My experience with commercial lighting is when the fixture is ordered or bought the specs should say 120/277. Then their wiring diagram should be...
Replies
7
Views
565

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top