Hi all,
Am wiring in some lights in a carpark..
The total distance is 150m
there are 4 lighting posts rated as follows A-200w B-300W C-300W D200W (with A closest to CU)
All loads are LED
They are spread at distances of
CU - A = 30m
A-B = 40m
B-C = 40m
C-D = 40m
Having done my volt drop calcs using 2.5 2c pvc armoured i get a total added Vd of 7.02
Firstly, if anybody can be bothered is this correct?
Secondly,I am aware that the regs state 6.9v as the highest allowed Vd... is there any breathing room with LED loads?
And lastly, if i do have to up my cable size, is it ok for me to use 4.0mm for the first leg of the circuit (CU-A), and then 2.5mm for the rest? This brings total Vd in at 6.
Any help appreciated,