Hi Guys,

could anyone explain to me the 1.2 volt drop rule of thumb? i understand the 3% for lighting and 5% for other circuits.
any help would be welcome studying for 2391.


Thanks in advance.
 
Hi Guys,

could anyone explain to me the 1.2 volt drop rule of thumb? i understand the 3% for lighting and 5% for other circuits.
any help would be welcome studying for 2391.


Thanks in advance.


I'd forget that rule of thumb job. Just do the calculation...length of cable run x design current x mV/m drp(from the appropriate big book table)

your %s are right.

Make up some imaginary circuits...100m run with 300Watt load, RFC in less than 100mm2(??)
then post your results.
 
You are right re the volt drop percentage.

The rule of thumb is for calculation ZS.

In the BGB it will give you ZS values for fuses mcb's ect you then multiply by 0.8 which will give you a lower figure.
This takes into account the the increase of resistance of the conductor with the increase of temperture due to load current and errs on the side of safety.
 
Hi mate volt is 3% lights and 5% power ie 6.9v lights and 11.5v power


asfor 1.2 do you not mean MF multiplying factor for increase in resistance due to operating temp for 70C cables when bunched or a core in a multicore Ie T/E
and 1.28 for xlpe 90C swa
 
the old 1.2 factor, I think he's getting confused with working out Zs sss, sod all to with voltage drop calcs

Depends how you're working it out.

If using volt drop tables you don't need it.

If you're working out by resistance then you do i.e ((mΩ/m x 2 x 1.2) x L x Ib) ÷ 1000
 
Last edited by a moderator:
The 1.2 is the multiplying factor used in volt drop.
If you measure resistance R1 + R2 at 20C or use tables measured at 20C you have to multiply the figure by 1.2 to give you the resistance at operating temperature 70C.
This R1+R2 *1.2 is then used in the equation V=IR.
.....I..... being the design current for the circuit or preferably the measured load current.

V is the volt drop along the cable.
 
The 1.2 is the multiplying factor used in volt drop.
If you measure resistance R1 + R2 at 20C or use tables measured at 20C you have to multiply the figure by 1.2 to give you the resistance at operating temperature 70C.
This R1+R2 *1.2 is then used in the equation V=IR.
.....I..... being the design current for the circuit or preferably the measured load current.

V is the volt drop along the cable.

Isn't that what I just said in post #6 :smiley2:

Depends how you're working it out.

If using volt drop tables you don't need it.

If you're working out by resistance then you do i.e ((mΩ/m x 2 x 1.2) x L x Ib) ÷ 1000
 
Guys thanks for all the input a big help.. bit clearer, im i right in saying the multiplying by 1.2 converts from ambient temp 20c to operating temperture of 70c?
 

Reply to volt drop rule of thumb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
676
  • Question
Ah OK, that makes sense. Thank you Avo.
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top