Hi,
I need to take a Supply from a house CU to an outbuilding which has a 20A radial socket circuit and 6A lighting. The cable run to the outbuilding is 20M then the lighting circuit inside the outbuilding is approx 10M in length and the socket cicuit 15M in length.
I'm trying to calculate a suitable size cable to be feed via a 32A mcb in the house.
Taking volt drop into account so that the full 32A can be utilised i have calculated that.
6mm feed 7.3 x 32 x 20 / 1000 = 4.67v
---------
1.5mm lighting circuit 29 x 6 x 10 / 1000 = 1.74v ------- > 1.74v + 4.67v = 6.41v < 3% 6.9v (ok)
-------- ---------
2.5mm socket circuit 18 x 20 x 15 / 1000 = 5.4v -------- > 5.4v + 4.67v = 10v < 5% 11.5v (ok)
------- ---------
so a 6mm 2 core swa would be suitable to supply this installation
Does this look good to you?
Thanks