Hi,

I need to take a Supply from a house CU to an outbuilding which has a 20A radial socket circuit and 6A lighting. The cable run to the outbuilding is 20M then the lighting circuit inside the outbuilding is approx 10M in length and the socket cicuit 15M in length.

I'm trying to calculate a suitable size cable to be feed via a 32A mcb in the house.

Taking volt drop into account so that the full 32A can be utilised i have calculated that.

6mm feed 7.3 x 32 x 20 / 1000 = 4.67v
---------

1.5mm lighting circuit 29 x 6 x 10 / 1000 = 1.74v ------- > 1.74v + 4.67v = 6.41v < 3% 6.9v (ok)
-------- ---------
2.5mm socket circuit 18 x 20 x 15 / 1000 = 5.4v -------- > 5.4v + 4.67v = 10v < 5% 11.5v (ok)
------- ---------

so a 6mm 2 core swa would be suitable to supply this installation

Does this look good to you?

Thanks
 
without double checking your sums, that looks spot on to me, although i don't think you'll pull more than a couple of amps on the lighting, meaning that you're on the right side.
 
Excellent,

The house earth type is tn-s, there's potentially a 2 steel roof brace that could be earthed. I was planning on installing an Earth rod to make it a TT system. what do you think?
 
use the TN-S. 3 core SWA and earth the armour both ends. as for the roof brace. determine if it's extraneous by testing to earth on 500V IR. if the reading is above 22k, ignore it. is there a water service into the outbuilding?
 
ok good thanks! From what i can see there used to be a service from a pvc pipe that's got a tap on the end, i presume it's been turned off at a stop cock before entering the building as nothing comes out the tap. There's no internal plumbing and no plans for it in the near future (being used as an office) so i guess i'm safe with exporting tn-s from the house.
 
Yea that's right although I'd like to design the sub feed in a way where the full 32A can be utilised in the circumstance of another circuit being needed.
 

Reply to volt drop in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top