Hi. I have a problem with an ATAG boiler. ATAG can supply their own tank sensor to accompany their boiler or alternatively you can use a volt free contact. The electrician who originally installed the boiler has correctly installed a 240v 8 pin relay of which the coil is energised via programmer and tank stat and the terminals that require a volt free contact are connected across the N/O poles of the relay. In my opinion this should work fine. BUT the boiler keeps giving a error code of E14 which according to ATAG is unwanted voltage on the terminals. I went to site and checked and with all cables disconnected and the coil energised there is indeed between 1.5 and 2.6 volts on the contacts to earth. I can only think this is being produced by magnetic effects of the relay coil. I have since changed the relays for Schneider mini contactors and bar 0.2 volts the affect is the same. I have been told to try solid state relays by a colleague. Any other suggestions?? Carlos