We got called to a house today for a minor works job.
TNC-S system, all electric night storage heating and immersion heaters.
While we were there we noticed our Volt Stick was lighting up on the pipework and cylinder in the airing cupboard.
The pipework was not live as we had been lent against it while working next to it.
The main bonding was in place to the water main, we tested continuity between the water main and the cylinder and pipework, it was fine.
The pipework was cross bonded fine.
We tested continuity between the main earthing terminal and the pipework, it was fine.
We then got interested and found that the Volt Stick only lit up on pipework in the immediate vicinity of the airing cupboard.
We then tripped off the mcb to each circuit in turn and found that the Volt Stick did not light up on the pipework when the lighting circuit was switched off.
We then pulled the lighting circuit out of the consumer unit and carried out insulation test on it, it was fine.
Carried out Ze, Zs tests, all fine.

Has anyone else experienced anything like this before?
 
mmm strange one! them volt sticks can be tempremental at the best of times but only getting the glow when the lighting circuit is energized! i was always lead to beleive the volt stick works on emf's and static when you rub it on ya trouser leg? could the pipework somehow be running in close proximity to a lighting cable and picking up some sort of emf this way??

rich
 
Thanks for your reply.
After talking about it today, we reckon that one of the pipes is resting heavily on one of of the lighting cables up in the roof.
Another sparky said that he had a similar volt stick light up on the fibreglass insulation in the roof, this was found to be caused by some flooring board squashing a lighting cable against a joist, when he removed the board, the volt stick stopped lighting up on the fibreglass.
Stange business isnt it.
 

Reply to Volt Stick Strangeness in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

My experience with commercial lighting is when the fixture is ordered or bought the specs should say 120/277. Then their wiring diagram should be...
Replies
7
Views
546
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
442

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top