The neutral conductor will only be neutral whilst connected to the neutral point of the supply, once it is disconnected from the neutral point it becomes just another conductor and will behave as such.
So if it is connected (via a load or fault) to a live conductor is will be at that potential with reference to earth or the neutral point. If it is not connected to anything but is in close proximity to live conductors it will have a capacitively coupled voltage on it which could be anything up to the full potential of the live conductors.
 
For the neutral of the lighting circuit to be live and give the electrician a shock it must have been disconnected from the neutral point of the supply allowing it to rise to a live potential.
This suggests either a borrowed neutral or incorrect isolation of the circuit.
If a light is switched off via the switch and not the MCB then all other lights on the circuit will still be using that neutral, so if the neutral is broken at the light being worked on one of the ends will become live. As an apprentice I did this exact thing on a lighting circuit in a conduit system.
 
The neutral conductor will only be neutral whilst connected to the neutral point of the supply, once it is disconnected from the neutral point it becomes just another conductor and will behave as such.
So if it is connected (via a load or fault) to a live conductor is will be at that potential with reference to earth or the neutral point. If it is not connected to anything but is in close proximity to live conductors it will have a capacitively coupled voltage on it which could be anything up to the full potential of the live conductors.
That is a far more eloquent way of saying what I was trying to say and makes far more sense!
 
Focus people. I'm asking a specific electrical question not asking for judgment. If there are gaps in the explainstion then show your experience and ask specific questions.
Murdoch- re read the OP. He switched off the circuit
Suffolkspark: Re read the last line of the OP. Happy to give more info. What would you like to know?

Hi bud,what i am focusing on,is that you may not have used the correct instrument,to determine the nature of those voltages.
 
Hi bud,what i am focusing on,is that you may not have used the correct instrument,to determine the nature of those voltages.

That wasn't directed at you. Sorry if I wasn't clear. Me and the guys in the company have a laugh about the Trade Forum version of Godwin's law. "How many posts until the inevitable accusation of not being a genuine sparks/plumber/engineer etc"
 
The neutral conductor will only be neutral whilst connected to the neutral point of the supply, once it is disconnected from the neutral point it becomes just another conductor and will behave as such.
So if it is connected (via a load or fault) to a live conductor is will be at that potential with reference to earth or the neutral point. If it is not connected to anything but is in close proximity to live conductors it will have a capacitively coupled voltage on it which could be anything up to the full potential of the live conductors.

Thank you mate. I'm really glad you could really understand my question. The capacitance of the disconnected neutral is the answer. I knew it was a flaw in the testing procedure but as I couldn't explain it like you I couldn't purseude the main electrical contractor.
 
Thank you mate. I'm really glad you could really understand my question. The capacitance of the disconnected neutral is the answer. I knew it was a flaw in the testing procedure but as I couldn't explain it like you I couldn't purseude the main electrical contractor.
Are you contending that someone got a bad shock off an isolated cable solely due to capacitive coupling to that cable?
 
Are you contending that someone got a bad shock off an isolated cable solely due to capacitive coupling to that cable?

No. He just explained the faulty test procedure I was doing which gave the voltage reading on neutral even once everything was disconnected.
The original fault which caused the shock would most likely have been a loose neutral somewhere on the circuit. This was corrected even if we never found exactly which cable was loose. The isolator is 4 pole, so maybe the neutral switch didn't connect properly when first switched on. The circuit was fully tested 3-4 times and what could be changed was, so I'm comfortable that the fault is no longer on the circuit.
 

Reply to the thread, titled "Voltage across neutral to earth" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
North London

Thread Information

Title
Voltage across neutral to earth
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
Obbit,
Last reply from
Obbit,
Replies
25
Views
9,036

Advert

Back
Top