I have 2 power sources.One is the Solar panels and the other is the Generator.
The solar panels Voltage output is 233V -228V but the generator gives 228V when there is no or small load and 210V when the big load is on.
The maximum load is 8KVA
So i want to install a voltage regulator to balance the two sources.

Is there any recommendations from where to buy and which one? What specifications i will need to pay attention?
This is my first V/R installation so i would need all the advises.

Thanks.
 
Section 7.10 of tyhe BRB is very specific on the control gear for PV systems .GN7 really spells it out as we. you will then have to tie theis in to the generator out but which will requier ballancing and possible a frequency rectifier. the PV cells generat D.C so an inverter reqiered there.
Its ounds like a complicated job so be carefull and possibly think about getting an expert it to give advice if you do the phisical work.
 
I have 2 power sources.One is the Solar panels and the other is the Generator.
The solar panels Voltage output is 233V -228V but the generator gives 228V when there is no or small load and 210V when the big load is on.
The maximum load is 8KVA
So i want to install a voltage regulator to balance the two sources.

Is there any recommendations from where to buy and which one? What specifications i will need to pay attention?
This is my first V/R installation so i would need all the advises.

Thanks.

Can you confirm you are running islanded as opposed to parallel with the Grid?

What size PV?

If Generator is only giving you 210V there is something wrong. What is the rating of the Generator?
 
Can you confirm you are running islanded as opposed to parallel with the Grid?

What size PV?

If Generator is only giving you 210V there is something wrong. What is the rating of the Generator?


Size of PV is 5KW
Is not parallel.We have only 2 sources, the Solar Panels and the Generator.The solar Panels is our main source.If the batteries goes empty then the inverter switch to the Generator.
When the Generator is On, it gives 228V and as the load increases the voltage is accordingly reduced.The Generator is 15KVA and the house's maximum load is 8KVA.
 
Surely your solar panels are charging the batteries via a charge controller so what do you need to balance the voltages for??

I want to balance the voltage range to 220V-230V and not have a big voltage difference.Now the electronics in the house is not safe when the voltage range falls from 233 to 210V
 
Is the system supplying the house with 230VAC from the inverters then changing over to Generator when the batteries get too low? Also, do the solar panels just charge the batteries?
A simple schematic of your system would be helpful. The generator should easilly be able to supply it's full voltage at it's rated power so i would suspect that the generator voltage regulation is at fault. Have you checked this?
One way around it is to use the generator to power high capacity battery chargers to charge the batteries when they're low thus the supply to the house always comes from the inverters
 
Last edited by a moderator:
Is the system supplying the house with 230VAC from the inverters then changing over to Generator when the batteries get too low? Also, do the solar panels just charge the batteries?
A simple schematic of your system would be helpful. The generator should easilly be able to supply it's full voltage at it's rated power so i would suspect that the generator voltage regulation is at fault. Have you checked this?
One way around it is to use the generator to power high capacity battery chargers to charge the batteries when they're low thus the supply to the house always comes from the inverters

The inverters switch to the generator when the solar power(batteries) have not enough energy left.
The generator charge the batteries and supply the house.When the batteries are recharged the inverter switch back to Photovoltaic.
My concern is, when the Generator is On the voltage is 228V.But as the load increasing the voltage drops.When the maximum load is on the generator produce 210V and sometimes 208V.So i have 20V drop.That is a 8% drop.
Like you said the voltage regulator of generator is probably the fault.
Thanks.
 

Reply to Voltage balance (two sources) in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
351
Need to crack on to get most from this year :cool: BTW if you are thinking about adding to the strings later, i.e. add more panels to existing...
Replies
6
Views
774
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
556
any idea why do I get the same voltage reading on the output AND input of the solar panel battery controller?
Replies
0
Views
785
  • Question
@Gareth Blackstock Please don't take my post as any kind of attack on your intellect, I made a very good point about these kinds of controls...
  • Gareth Blackstock
  • Australia
  • 15
  • 2K
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks