Hi

If anyone can help,I am carrying out an EICR on part of large hospital and have found voltage that varies between 100 and 200v between live and neutral on one single phase submain cu. It is present when main switch is off so is on load side. Apparently they get voltage around 0v to 60v sometimes due to machines connected on a particular circuit but I have isolated what i can and still getting this voltage. Any ideas, cheers
 
Firstly be aware the hospitals may in certain areas utilise IT earth arrangement. Have you established for sure what earthing arrangement you're dealing with?

Forgive my ignorance but this is the 2nd time you (I think) have said use an analogue meter, whys that? And can you even buy one readily as I've not seen one in years.
Analogue tester are not fashionable but they're available from all major suppliers. Every electrician should have one. They have a lower input impedance so they don't give confusing readings where capacitively coupled or induced voltages may be present.
 

Reply to Voltage between Cpc and neutral in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
826
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
948

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top