W

Will Sykes

I was called over to check out why some corridor lights kept tripping out. They are all on klik roses, wired in singles inside metal trunking. I turned the circuit off and disconnected all cables in order to test for insulation resistance. Before i even got a chance to test, i found that the voltage between Live and Neutral was 189v, between Neutral and cpc was 215v and live to cpc was 0v. Any ideas why i could be experiencing these voltages? At first i thought there may be a shared neutral somewhere.
 
sounds like a floating neutral or something like. isolate compete board and then do dead tests. check for cross connections between circuits and for any open circuits.
 
Most likely a shared neutral, I would expose the entire circuit if it's in trunking, the fault should be easy(ish) to find.
 
"live to cpc was 0v" i would suggest there is a broken connection in phase or cpc or both.dead test is the first thing i would do ..wander lead to check continuity or short R1 TO R2 in Board and test from a mid point to split the circuit in half.so you know which half has the fault.
please feel free to comment im not an expert :) even some +ve feedback would be nice.
 
found the fault. indeed someone had pinched a neutral for two neons in a bank of switches. didn't notice it at first as the switches were not for the lights at fault. problem with where i work is that it is for a pharmaceutical company and therefore most things cannot be turned off without it being planned into our six monthly shutdown periods.
 
good grief.that cant have been easy to find.not usual is it to find any neutrals in a switch bank.even harder for practical terms without been able to turn things off.Cant you even isolate power out of normal working hours?
If i was the maintenance manager i would have been very impressed by your diligence.:)
 

Reply to Voltage between Neutral and CPC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
681
  • Question
Thanks again, I’m sure I’ll be back with many more questions
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top