Evening all hope your all avoiding the nasty bugs that are going round! I'll keep it brief, got called out to a bungalow that had a ceiling rose pendant that was flickering after being switched off. Testing it I found 10 volts at the switch live when switched in off position, 230 when on. Fiddled about for a while and had a look above (it is accessible being a bungalow) bit of a head scratcher really. All in all got a bit confused so put everything back together and said will go back in the morning, light wasn't flickering when I left!. Not major but just very annoying...any thoughts much appreciated. Was wondering about an induced voltage from something elst but all the cables in roof seem sufficiently far enough away from other things.
 
Sounds very like induced voltage.

Was the lamp an energy saver fluorescent?

Was the light on a 2 way switching arrangement?


Sent from my iPhone using Tapatalk
 
Yes to energy saving flourescent however voltage there even without lamp inserted...yes to 2 way switching although abit old school (for me) in singles and T+E
 
Ok 2 remedies that I know of.

Change the wiring of the 2 way switching to the conversion method if it is wired in the conventional way.

Or fit a snubbed between switched L & N at light fitting.



Sent from my iPhone using Tapatalk
 
Ok 2 remedies that I know of.

Change the wiring of the 2 way switching to the conversion method if it is wired in the conventional way.

Or fit a snubbed between switched L & N at light fitting.



Sent from my iPhone using Tapatalk

Sounds great Sintra, what's a snubbed? Some sort of spike protector? Apologies for my ignorance!
 
new guy here. query i have, can a snubber, fitted within a device, in our case electric blind motors, have any influence on rcd tripping, in particular if several motors all started (or stopped), at the same time
 
Hi Robd,

how did you get on?

Did you order some?

If not I will hapilly post you one of mine, as I have a few and rarely use them!

PM your address and next time you see an air ambulance collection pot drop a couple of quid in it as payment!!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

robd

Arms
-
Joined
Location
East Anglia

Thread Information

Title
Voltage down switch wire, switch off. Help!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
robd,
Last reply from
robd,
Replies
17
Views
4,161

Advert

Back
Top