I'm having a bit of a blonde moment, I'm trying to work out the volt drop on a 3 phase Submain, the Submain is to be supplying a 3phase board loaded with rcbo's all single phase loading, I can't for the life of me remember how to do it I think it's working out the single phase vd and multiplying by 0.86 but have gone blank! Any help appreciated
 
Ah right ok so that's already done on the stated values that makes sense, so if I use the largest load and work out volt drop on that value ( it's a very hard one to balance as swimming pool is pulling a large load on one phase and circuits are spread out on the other 2 phases) thanks alot
 
Assume the worst if its that unbalanced and treat the sub main and final circuit as both having a neutral volt drop. (2-core)

So use the largest load and use the vd figures for 2 core cable out the bgb? Its the neutral size I'm concerned of iv always been told keep it the same size as the phase unless if cost is an issue then start calculating to see how small you can get it!!
 
I personally would keep the neutral conductor the same size regardless of the savings. To reduce the neutral requires a very precise design knowing all the constant phase loadings etc. Then applying this formula to determine what current will be drawn by the neutral.

In=√((IL1²+IL2²+IL3²)-((IL1xIL2)+(IL1xIL3)+(IL2xIL3)))
 
Sub boards out on the plant. It's no different to what you're doing, just needs a few more animals to pull the cable in.
25mm or 240mm it still needs just the same skills to make off correctly. You just need the animal power :90:
 

Reply to Voltage drop and 3phase in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...
Replies
2
Views
1K
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
86

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top