Hello all, just been thinking over Voltage drop!!

1. Where does the 3% and 5% figures for voltage drop (VD) come from? Appendix 4 (BS7671) gives the figures but why the different values between lights and sockets?

2. Also permitted voltage levels are -6% and +10% from 230V giving a min of 216V and max of 253V. If these permitted figures allow a voltage as low as 216V why can voltage drop only be 3% for lights (i.e bringing it down to 223.1V)?

Cheers..
 
The ESQCR percentage tolerances allow for the supply to reach your consumers terminals. You then have to ensure that the additional voltage drop in the installation is within limits.

Typically, lighting is more seriously affected by voltage drop. Fliament lamps especially, as the voltage falls not only does the light output decrease very rapidly but also the efficiency. So if you fit more / bigger lamps to counteract the loss of output, the consumption is increased. Compare electric heaters, where although the heat output reduces with the square of voltage, the efficiency remains constant, so under thermostatic control the element is just on for longer. Switched-mode power supplies will use the same amount of power regardless, as will some motors. And as mentioned above, discharge / fluo lighting is often one of the first things to fail altogether at the voltage falls, if it cannot strike.
 
Although bs7671 states 230v as the nominal single phase voltage for design calcs , no way does the dno use 230v as their baseline figure for distribution.
hence 9 times out of 10 the voltage at the terminals of a domestic cut-out is 240 or higher.

and the regs take into account that all of this is out of the installers / designers control and dont insist on a lower / tighter volt drop limit thats reliant on the dno voltage value , which could result is ridiculously oversized cables in trying to comply.
 
I think DNO transformers are still normally set up for 440/250V

This is why the argument about standardising the supply at 230v is wrong,to drop the voltage at the transformers would lead to an increase in the current across the network,which would cause major problems.In fact I don't think I have ever measured 230v at a house,they are usually around the 240v mark,I,ve actually had it as high as 253v in my house.
 

Reply to Voltage drop and it's effect? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top