can anyone tell me if this is a correct way of thinking
i have 6 Cleaners outlets off a !6a rcd, total run length is 55m
6mm feed to first point is 30m would give me voltage drop of .78% (using half the breaker load according to exception 1 on page 163 of as 3000:2018)
then run a 2.5mm for the remaining 25m giving me a voltage drop of 1.56% (same exception)
total voltage drop of 2.34% ( i need to be under 3 for this installation)
my main question being is it acceptable to break gauge considering the breaker protects the 2.5mm cable as i cant seem to find it in the rule book