In answer to your core question that relates to the deviation from the length of standard final circuit designs in the OSG set against your calculations.
The standard final circuits in the OSG assume certain parameters. For a 6A 60898 the Ib of the circuit is based on a load of 5 Amps. You have an Ib that you have used of 2.38 Amps.
Side point: With a lighting circuit with a [reasonably] evenly distributed load the design current is [generally] divided by 2 in the volt drop calculation.
Take into account that your mV/A/m figure for T & E of 29 is based on a conductor operating temperature of 70 deg C . The design current of your circuit (2.38 Amps) is significantly less than the effective current carrying capacity of the 1.5mm cable - hence resistance values will be less than shown.
In this case the 29 mv/A/m figure will give a calculated VD erring very much on the side of caution . The exact value can be calaculated using the factor Ct if required.
[If you don't want to go Ib/2 then simple radial calculation of Ib load at extremity of your circuit]
The standard final circuits in the OSG assume certain parameters. For a 6A 60898 the Ib of the circuit is based on a load of 5 Amps. You have an Ib that you have used of 2.38 Amps.
Side point: With a lighting circuit with a [reasonably] evenly distributed load the design current is [generally] divided by 2 in the volt drop calculation.
Take into account that your mV/A/m figure for T & E of 29 is based on a conductor operating temperature of 70 deg C . The design current of your circuit (2.38 Amps) is significantly less than the effective current carrying capacity of the 1.5mm cable - hence resistance values will be less than shown.
In this case the 29 mv/A/m figure will give a calculated VD erring very much on the side of caution . The exact value can be calaculated using the factor Ct if required.
[If you don't want to go Ib/2 then simple radial calculation of Ib load at extremity of your circuit]