A
adamh
I need to fit an armoured cable to feed a few outside lights the run is 130m and the load will be 6 amp.
from the OSG i can see that 2.5mm multicore pvc single phase will drop 18mV, 4mm 11mV and 6 7.3mv
ive done the calculations
mV x 6 x 130 / 1000 = 14.04V
mV x 6 x 130 / 1000 = 8.58V
mV x 6 x 130 / 1000 = 5.69V so clearly its 6mm cable required on a 6 amp mcb
when i do the calcualtions using the ressiatance of copper at
1.78X10-8 x 260 / 2.5 X10-6 = 1.85ohms x 6 amps = 11.1V
4mm = 6.942
6mm = 3.06V
As its lighting im looking for no more than 6.9V with a Uo of 230V
now would you go with 4mm using the ressistivity values calculated and rounding to 1 decimal place
or 6mm using the OSG table 4D1B i did check the figures in the BGB for pvc swa and they are the same.
ive not used the adiabiatic to check the earth and another possibilty would be a 3A FCU to feed the c/ct and recalculate?
from the OSG i can see that 2.5mm multicore pvc single phase will drop 18mV, 4mm 11mV and 6 7.3mv
ive done the calculations
mV x 6 x 130 / 1000 = 14.04V
mV x 6 x 130 / 1000 = 8.58V
mV x 6 x 130 / 1000 = 5.69V so clearly its 6mm cable required on a 6 amp mcb
when i do the calcualtions using the ressiatance of copper at
1.78X10-8 x 260 / 2.5 X10-6 = 1.85ohms x 6 amps = 11.1V
4mm = 6.942
6mm = 3.06V
As its lighting im looking for no more than 6.9V with a Uo of 230V
now would you go with 4mm using the ressistivity values calculated and rounding to 1 decimal place
or 6mm using the OSG table 4D1B i did check the figures in the BGB for pvc swa and they are the same.
ive not used the adiabiatic to check the earth and another possibilty would be a 3A FCU to feed the c/ct and recalculate?