trying to get the right table in the BS7671 book and the On site guide, regarding wroking out my CCC and VD....
I worked out my design for my shed, its going in twin and earth flat, in round conduit. Looking in the BS7671 it looks to me that is a Method B.
There isnt a method b, on the flat cable in either book. I thinking its going to be multicore cable PVC.
so been looking at table 6D1 OSG & 6D2 But when working out VD on using 2.5mm T&E, using 32amp MCB, and is only 20m cable to be used.
When working out the VD im getting weird answers and getting 5% dead on volt drop.
my calculation for my ring is:
mV/A/m so. VD= (18x32x20)/1000 = 11.52
11.52x100/230 = 5% dead on
Am i right, or am i just being plian stupid somewhere and gone absolutly wrong....