hi guys

trying to get the right table in the BS7671 book and the On site guide, regarding wroking out my CCC and VD....

I worked out my design for my shed, its going in twin and earth flat, in round conduit. Looking in the BS7671 it looks to me that is a Method B.

There isnt a method b, on the flat cable in either book. I thinking its going to be multicore cable PVC.
so been looking at table 6D1 OSG & 6D2 But when working out VD on using 2.5mm T&E, using 32amp MCB, and is only 20m cable to be used.
When working out the VD im getting weird answers and getting 5% dead on volt drop.

my calculation for my ring is:

mV/A/m so. VD= (18x32x20)/1000 = 11.52
11.52x100/230 = 5% dead on

Am i right, or am i just being plian stupid somewhere and gone absolutly wrong....
 
hi guys

trying to get the right table in the BS7671 book and the On site guide, regarding wroking out my CCC and VD....

I worked out my design for my shed, its going in twin and earth flat, in round conduit. Looking in the BS7671 it looks to me that is a Method B.

There isnt a method b, on the flat cable in either book. I thinking its going to be multicore cable PVC.
so been looking at table 6D1 OSG & 6D2 But when working out VD on using 2.5mm T&E, using 32amp MCB, and is only 20m cable to be used.
When working out the VD im getting weird answers and getting 5% dead on volt drop.

my calculation for my ring is:

mV/A/m so. VD= (18x32x20)/1000 = 11.52
11.52x100/230 = 5% dead on

Am i right, or am i just being plian stupid somewhere and gone absolutly wrong....

Firstly, the CCC table you want in the OSG is 6E1 (page 131).

2.5mm² T&E Reference Method B is 23A. The CCC of a ring circuit is taken as 40A (20A per leg) so 23A is sufficient.

To work out the VD for a ring you use 26A (see page 54 OSG) as the design current so the calculation would be:

(18 x 26 x 20 Ă· 1000) Ă· 4 = 2.34V (1%)


It is also worth remembering that the maximum length of a ring circuit for voltage drop is 98m at ambient temperature of <30°C and 106m at ≥30°C

4 x (11.5 x 1000) ÷ 26 ÷ 18 = 98m (<30°C)

4 x (11.5 x 1000) ÷ 26 ÷ 18 ÷ 0.923 = 106m (≥30°C)


The 0.923 in the second calculation is the correction factor for the reduced operation temperature of the cable (Ct) when it's not carrying its full current capacity (see page 258 BS 7671) but is only applicable at an ambient temperature ≥30°C.
 
Last edited by a moderator:
Hi JUD if i am reading this correctly Danny is running a ring from his CU to his shed through a single conduit? ie both legs does this mean that there would be a derating of 0.8 for grouping involved - or would that not be relevant in this case? ( I appreciate it won't affect the overall design as there was a lot of slack , but was just wondering)
 

Reply to Voltage Drop issue in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
937
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top