Hi folks Iknow this topic has been beaten to death on this forum but after reading some of the posts and speaking to some of my co workers I am still a littleconfused, I am aware there is several ways of calculating voltage drop but amstill unsure of when to use the correction factor of 1.2 and when to leave itout I have some examples below could you folks look at them and tell me if theyare the correct methods and when to use the 1.2 and when to leave it out. Thankyou
16 X .29 = 4.64 v
- Calculate the voltagedrop for a 2.5 cable supplying a radial socket 22 meters long operating at anambient temperature of 30°C and having a operating temperature of 70°C and adesign current of 16 Amps the voltage drop is 18 mV/A/m, calculate the overallvoltage drop
Voltage Drop= (mV/A/m) x Ib x L
1000
Where mV/A/m= milivolts per amp per meter.
IB- is the design current.
L -is the length
Voltage Drop
18x 16 x22 = 6336 mV
6336/ 1000 = v
6.33V
- Ifa 10mm 3 core cable has a length of 80meters and is supplying a 9KW shower at avoltage of 230volts, operating at 20°c. Conductor resistance for 10mm copperconductor is 1.83mΩ/mtr
Voltage Drop = (r1 +rn)x L x Ib
Voltage Drop = voltagedrop
(r1 + rn) = Conductorresistance
L = Correctiontemperature (30°) (1)
L= Correction temperature(20°) (1.2)
Ib = Circuit RatedCurrent
9000/230 = 39.13A so theBreaker size 40A
1.83mΩ/ mtr x 80 = 146.4m Ω
146.4/1000 = 0.146Ω and 0.146 x 2
(r1 + rn) = 0.2928 Ω
Vd = (r1 +rn) x L x Ib
(0.2928) x 1.2 x 40A
= 14.05 V
- A radial circuit is fed from a 16A mcb the value of the combined conductors are 0.29ohms,calculate the volts drop for the circuit, and determine if the value isacceptable?
16 X .29 = 4.64 v