Hello guys looking in,
Just want to make sure i'm doing this right as i'm still a bit fresh,
This is the senerio as follows,
Single lighting circuit from a 230v supply on a 10 Amp MCB.
1.5mm PVC Singles total length from board to furthest point 40 metres.
1500 total watts of various lamps being used in 6/8 rooms and corridor area.
Is the calculation as follow,
Size of cable x the Amps being used x the distance of the cable, devide by 1000 to give the volts
I'm not not sure about the rest basically is the voltage drop of the above within 17th edition is it 3 per cent i'm reading 6.9v in my on site guide ?
Any clarification appreciated on getting me right on this, thank KB