Hello guys looking in,

Just want to make sure i'm doing this right as i'm still a bit fresh,

This is the senerio as follows,

Single lighting circuit from a 230v supply on a 10 Amp MCB.

1.5mm PVC Singles total length from board to furthest point 40 metres.

1500 total watts of various lamps being used in 6/8 rooms and corridor area.


Is the calculation as follow,

Size of cable x the Amps being used x the distance of the cable, devide by 1000 to give the volts

I'm not not sure about the rest basically is the voltage drop of the above within 17th edition is it 3 per cent i'm reading 6.9v in my on site guide ?

Any clarification appreciated on getting me right on this, thank KB
 
OK Looking at my on-site guide and the information i have above the voltage drop per amp per metre for 1.5mm is 29 (page 130 table 6d2)

So using my info listed above would i do

29 x 6.52 x 40 / 1000 = 7.56 v

if this is right i'm only allowed 6.9 v

so my voltage drop is too much??
 
Hang on is it,

29 x 40 / 1000 = 1.16v ?

so i'm well within ?

I think i was right the first time looking at the guide again can any one just confirm that for me, thanks KB
 
Last edited by a moderator:
Hang on is it,

29 x 40 / 1000 = 1.16v ?

so i'm well within ?

I think i was right the first time looking at the guide again can any one just confirm that for me, thanks KB

No. You were right the first time.

29 x 6.52 x 40 / 1000 = 7.56V (3.29%)

You would need to use 2.5mm2
 

Reply to *Voltage drop Question Calculation help* in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top