Sorry for raking it up again but it's interesting. Table 7.1(1) latest OSG gives a maximum length of cable as 59m for 1.0mm with ref method 101 on a type B 6a mcb. Table F6 OSG gives ccc of 1.0mm with ref meth 101 of 10.5a and vd of 44mV/A/m. But the cable length permitted doesn't work out if you calculate the vd with an Ib of 6a and cable length of 59m. 44 x 6 x 59 / 1000 = 15.58v which is way in excess of 6.9v (3%). Or have I picked this up all wrong?

What I'm trying to say is that the values in Table 7.1(1) for maximum length have probably..... taken into account that the lighting load will most likely be a lot less than 6amps and that this load will be spread out along the length of the circuit and not all lumped at the end. Hence using the standard volt drop calculation with full load and maximum distance will not equate to this standard circuit value. At the end of the day it is only a guide and doing your own calculations will give you a much more accurate value.
 
The drop increases along the cable run dependent upon the load applied to it i.e., lighting points and longer cable unlike a shower circuit where all the load is applied at the far end? And the tables for vd in lighting circuits account for this probability?
 

Reply to Voltage Drop in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
499
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
385
I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...
Replies
24
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top