We are all familiar with the requirements for measuring Zs and verifying that it is within the limits for the particular type of protective device. I use a single guide of 1.2 ohms as the maximum though there are of course many variations.
What we (I) have not been noting is (R1+ Rn) and the implicite voltage drop associated with it.
A quick calculation shows that if Zs for a ring circuit were 1.2, and we assume a generous 0.20 for Ze,
Then R1+R2 = 1.0, and assuming the circuit wired with 2.5/1.5 then R1 = 0.4 so (R1+Rn) = 0.8.
Now 0.8 ohms at 32A gives a voltage drop of 25.6 volts. MORE THAN DOUBLE that allowed for power circuits.
So should we be looking for a maximum Zs of 0.48 ohms to ensure the voltage drop requirement is satisfied?