R

Robo

6.9 v for lighting
11.5 for a socket.

So my question is to calculate the size of a supply cable to a building that had lighting power heating for example. What figure would i use for voltage drop.

Is there a wxtra safe rule of thumb method ppl use?
 
id use the 11.5v mate. its not just sockets its everything other than lights. to the best of my limited knowledge the vd limits are because light fittings some times have voltage sensitive equipment.
 
6.9 v for lighting
11.5 for a socket.

So my question is to calculate the size of a supply cable to a building that had lighting power heating for example. What figure would i use for voltage drop.

Is there a wxtra safe rule of thumb method ppl use?

If the sub main has both lighting and power as final circuits then you need to use the figure of 6.9V or 3%. This has to be the maximum volt drop from the origin to the last point on the lighting circuit.
 
Voltage drop is monitored to ensure that loads are not deprived of too much of their operating voltage due to cable resistance.

Each final circuit will be treated independently, whilst distribution circuits may need further consideration.
 

Reply to voltage drop. in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
271
  • Question
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top