Voltage drop | on ElectriciansForums
Discuss Voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
P
pencilpusher
Hi all
If an outdoor circuit comprises 2.5mm SWA running to adaptable box where it then splits into 2 x 1.5mm SWA cables for lighting, socket etc. how is the VD calculated?
I presume the VD for the 2.5mm run is calculated up to the adpatable box and added to the 1.5mm VD for each additional cable run present?
I would normally calculate on the smallest cable size present as a worst case scenario but was wondering what the alternative way is for the cables present.
PP
Supposing though that at the end of each leg of the smaller cable you had the same load, then wouldn't it be conductors in parallel? For arguments sake, if it was a 100W lamp, then wouldn't you be doing the calcs based on 200w down 3mm?? (also assumes both legs the same length).
Mostly voltage are drop at your homes because of the more than load of energy when you use the energy overloaded then you face the drops of voltage
Please may we have that again, only in English this time?
I know what voltage drop is and why it occurs. I don't, however, understand a word of this!
Hmmm, this has got me thinking now! Views?
PP
It gives the same VD...
haven't done the maths so happy to be corrected, but if you go by the BGB tables then they are non-linear, so not sure about that.
Yes, in my tables the resistivity differs between 18.1-18.3 mΩmm²/m depending on the csa. But there is no meaning in trying to calculate the VD with a mV precision.
Thanks but that is not the point though. My OP was about the correct way of doing it, not weather it was worth bothering with precision. I will stick with adding the VD up as previously mentioned.
^^^ agree entirely. But it's been a slow day here at Rockingham Towers, so......
I thought voltage drop was what happens when the CU is upstairs, and all the sockets and lights are downstairs, so the volts all drop down the wires to the electrical stuff. Anyone know where my electric stopcock is?
Cheers.........Howard
should be in the attic. water flows downhill as well as volts.
Reply to Voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...