deller
tested a circuit and its measured voltage was 218V. No where near the calculated VD. Any suggestions on what the Maximum permissable VD is .
cheers
Lighting or power?
Also, what was your voltage at the main CU?
It's 5% of power, and 3% of lighting, therefore 218.5V and 223.1V working at a nominal voltage of 230V to earth.
lighting 3% 6.9vsockets 5% 11.5v from origin of the supplyhope this helps
cheers
Reply to voltage drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...