Advice needed please, I was called out last week to a nuiscance tripping problem with an old elcb, IR tests showed up a L-E fault on ring circuit, finaly traced the fault to a wall light run off ring circuit which was shorting out in the socket. I disconnected this, put everything back together ,carried out tests again and had good results. Happy days!
I had a phone call today , its tripping again!! it was ok all weekend.
Going back tomorrow for another look, do some more testing, pat test the appliances etc, is there anything else I should be looking at, any ideas welcome. Are these old trips prone to tripping, is there any way it can be tested.
Thanks in advance.
 
Thanks for the replies, they will be having the c.u. replaced fairly soon. Carried out some more testing this morning, they have a surge protector extension lead with 0.3 Meg ins. test , disconnected this and hopefully no more tripping.
 
0.3M is usually a neon light.

corect me if I am wrong but if only 1 main RCD it should be a time delay unit (normaly 100mA as well) do you guys actually replace these old voltage "rcd's" with 100mA time delay RCD's or just put in a 30mA std rcd? I ask since the time delay ones are quite pricey. I tend to convince the owner to go for a new dual rcd board, especially when comparred to the cost of a time delay 100mA.
 
FYI

Testing a VOELCB for correct operation requires the use of a double wound transformer having an output voltage not exceeding 50V rms a.c. to be applied across the neutral and frame terminals of the VOELCB. The object is to check that the device trips 'instantaneously' (which is defined as being with 100ms in BS 842, the product standard for VOELCB's).

Anyone here got one of those in the van?


Me neither.
 
A Short term solution is to replace with a 100ma RCD (£18.33 Inc VAT from TLC Direct) and a 2 Module Enclosure (£4.69 Inc VAT from TLC Direct) and advise that a board change is required. That way you've left it no less safe than it was. But usually where there's a ELCB there's a wylex board, so if they can afford it, CU upgrade.
 
FYI

Testing a VOELCB for correct operation requires the use of a double wound transformer having an output voltage not exceeding 50V rms a.c. to be applied across the neutral and frame terminals of the VOELCB. The object is to check that the device trips 'instantaneously' (which is defined as being with 100ms in BS 842, the product standard for VOELCB's).

Anyone here got one of those in the van?


Me neither.


Funny you should say I do have an old Clare tester secreted among other dilapidated items of rubbish in my garage, perhaps i'm waiting for all this stuff to come back in vogue.

If you supply the batteries, and get it calibrated, oh how I miss non calibrated days, then it's hirable for a small fee widdler ;)
 
Funny you should say I do have an old Clare tester secreted among other dilapidated items of rubbish in my garage, perhaps i'm waiting for all this stuff to come back in vogue.

If you supply the batteries, and get it calibrated, oh how I miss non calibrated days, then it's hirable for a small fee widdler ;)
try it on ebay under antiques and collectables
 

Reply to voltage operated elcb, nuisance tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K
  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top