Does anybody know the requirements regarding voltage regulation with DNO..
Does the supply voltage need to be maintained within a required percentage?

Been to a customer today thats having problems with electrical devices in the home because of poor voltage regulation. I got readings between 190v and 310volts.. Seems worse during times of high demand.

After chatting with the neighbours either side they seem to be having the same problem.
 
230V

+10% at 253V
- 6 % 216.2

between those ranges

BS7671 APPENDIX 2 - 14.

better wait for the experts to reply about possible reasons why you might be getting terrible voltages and what to do about it, I'd ask the supply company.
 
Last edited by a moderator:
Customer did contact supplier and got the impression they wouldnt do anything about it because of cost rectifying this.
Give them the excuse that its because there at the end of the supply cable.
 
Stevie is absolutely spot on. Let your customer know that they can go back to the supply company and quote back that regulation to give them a bit of ground to stand on.
 
Wouldnt variation beyond the declared values of tolerances be considered a breach of the Electricity Safety, Quality and Continuity Regulations 2002 under section 27 which specifies the nominal values of frequency and voltage together with permitted tolerances?

I think they're just trying to fob you off.
 
Would hazard a guess at either the Neutral having a dodgy connection somewhere along the line or one of the users having an earth fault on one of their phases. Either way, the DNO is outwith their legal supply limits and are at fault here.
They may need to get some form of recording the data over a period of time though to put evidence to the DNO, so it could involve getting a Dranetz power quality meter or one of the fluke scopemeters involved. Not cheap, the last Dranetz we hired was £750 a week !
 
Those voltages indicate a major problem, as others have said ring the dno's emergency number. You can find your local dno on the national grid website.
 
Yes call the DNO NOW and ask them to measure and put on a voltage recorder. I got them out when it was only 256 volts and they pulled the fuses at the local transformer within 3 hours of the call. If they still won't listen go hire a Fluke VR101S and ir will give you all the readings you need. If you are interested in seeing the power quality in the building have a look for a Fluke 43B, these items can be had for about £70 to £100 per week.
 

Reply to Voltage regulation. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

  • Question
I'd start by doing the usual supply impedance tests followed by N-E voltage with the installation under some load. Also visually inspect and...
Replies
4
Views
1K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top