After some advice please, I`m gas safe registered and have to do safe isolation to TB118. It`s a new build site and the fast blow fuses were blowing on the boiler; the spark said it was a problem with the boiler. Put a temp on the boiler and it works. On doing a dead test on earth to live on the supply, I`ve got a Di-Log 6780-volt tester the red AC and green L light up, I`ve not come across this before and with the fuses blowing on the boiler I would expect the continuity to light up.
I`d like to know the reason for this so that I can look out for it in future, Thanks for any help.
 
I'm no expert as I do not own this model but probably similar to my Fluke. For the AC light, I guess you must be picking up voltage this will illuminate for AC or DC volts, Maybe just to warn you that there is very low voltage present below 12 volts. Did you try reversing the probes ? The L would be indicating AC single-phase voltage. If DC voltageI guess it would show as polarity + or -.
 
If you test live to earth you will get a live reading in any event. I imagine you have a TN- system so neutral and earth are connected at the incomer/cut-out so you will make a circuit the same as the L-N test.
 
Thanks for the replies, the electrician removed the lives from the RCD, and I was getting the same reading at the board L to E, but I recall that there were 2 lives which to me is indicating a ring circuit and the heating is supposed to be on its own supply. I`ll check on Monday, if it`s not been fixed.
It`s what`s causing light sequence if there is no power to the circuit, that i don`t understand.
 
I use a di-log voltage tester as my main safe-isolation tester.

The single red and single green LED will illuminate in the presence of a phantom/ghost voltage.
If an actual voltage is present you will see the relevant red voltage level LEDs.

The continuity function has a threshold of 2Kohms so any impedance greater than this will not illuminate the yellow LED.
 
According to the spark, the fault is on the neutral, still don't understand why both fast blow fuses would blow on the boiler.
Thanks for your replies.
 

Reply to voltage tester show sequence of lights. in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
456
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
Just doing some thread admin :)
Replies
1
Views
919

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top