Understood, thanks Andy.Section 412 is relevant to double insulated systems only.
aDon't you guys read the//Why not just a large enough adaptable box with wago din push in things? Trunking either side of it if theres space?
Because if you know the joint is in the CU then, not far to look for it, however in trunking where do you start looking?Surely it's no different to extending a T&E inside a consumer unit using some wagos, etc. where it's a bit short. And the joint is accessible by just popping the trunking lid off, which is no more difficult than opening an MF enclosure.
Is 412.2.2.3 relevant in this case? My thinking is the trunking lid can be removed without a tool and the Wago connector is not IP rated.
Those terminals will still be IP2X though.It's an interestring point. However, "devils advocat" - it's possible to remove the grille of a 600x600 flouresent (and most 4ft and 5ft's) to access live terminals. Eithert by undoing a knurled screw on the 4/5ft's, or simply sliding the diffuser out on a 600x600....