Noob2013

Hey all, just a quick one.

I'm doing some work on a property and noticed the gas and water are not bonded with 10mm. The water has been bonded from a junction box!

The incoming water supply comes in from the main road in copper but runs straight from the stopcock in plastic.

What's the situation regarding bonding?

Do I bond before stopcock, find the first section in copper or is it not a requirement?

Thanks
 
Does it require bonding?
That's where I would start.
Bonding of an extraneous conductive part is a requirement.
All you have to do is prove if it is or not.
What work is being carried out at the property?


Sent from my iPhone using Tapatalk
 
Is that by testing insulation resistance on 500v between the earth terminal and metallic pipe and if the reading is greater than 23,000 ohms then it is not required? . I have jug read this from another post on here.

Where would I test? The incoming copper supply or the first bit of copper after the plastic from the stopcock?
 
Is that by testing insulation resistance on 500v between the earth terminal and metallic pipe and if the reading is greater than 23,000 ohms then it is not required? . I have jug read this from another post on here.

Where would I test? The incoming copper supply or the first bit of copper after the plastic from the stopcock?

Taking 10mA as being the dangerous fault current then 230v/0.01mA gives you 23,000 ohms, taking 1,000 ohms as average body resistance into consideration. Using an insulation resistance will mean you will recieve your answer in Mohms so your looking at figure of 0.022Mohms. Depending on your test instrument it may only give you three decimal place reading but is a good indication.
Test between MET all cables apart from suppliers earth disconnected to whatever part in question, to find if it is infact extraneous conductive part or a lump of metal.
 
Thanks.

Would this include the incoming water before the stopcock or just anything after the stopcock? It enters the property on copper and straight out in plastic so if I had to bond the incoming water then it would have to be done before stopcock.
 

Reply to Water Bonding Query in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
701
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
376
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top