Hi,

I have to bond the water and gas on a TT installation, the electrode has a 10mm/sq to it already. Its my mate`s house and I`m adding a new lighting circuit for my DI assessment. My mate has got some 16mm/sq G & Y lying around. Can I use this to bond the gas & water while the main protective conductor remains at 10mm/sq?

Thanks
 
I *believe* I'm right in saying that the conductors on a TT system only have to be 4mm max if they're not buried so you can do what you like above that.
 
with the price of 16mm, i'd save it for main earthing on other jobs and buy some 6mm for this one.
 
the CSA of the earthing conductor in TT installations is governed by the Ra of the rod. the lower the resistance, the higher the fault current, and the larger the cable needs to be as a result.
 
I'll hold my hands up to knowing little about TT requirements (through necessity) and even after having a look through the OSG I can't find 6mm mentioned. Could you point me in the right direction please? :)

Minimum CSA for earthing conductors, is 2.5mm² (if sheathed).
Minimum CSA for bonding conductors, is 6mm².
 
I did a Ze test a while back on this one and got a reading of about 150 ohms which to me is ok ( under the 200 ohm mark ). It was the 16mm gas and water I was wondering about.
How does that sound mate?
 
I'll hold my hands up to knowing little about TT requirements (through necessity) and even after having a look through the OSG I can't find 6mm mentioned. Could you point me in the right direction please? :)
"544.1.1 Except where PME conditions apply, a main protective bonding conductor shall have a cross-sectional area not less than half the cross-sectional area required for the earthing conductor of the installation and not less than 6mm²."
The 2.5mm² is mentioned in Table 54.1 and Regulation 543.1.1.
 
I did a Ze test a while back on this one and got a reading of about 150 ohms which to me is ok ( under the 200 ohm mark ). It was the 16mm gas and water I was wondering about.
How does that sound mate?

personally 150 ohms would be the limit, yes its fine but anything higher i would defo consider extending or adding another spike.
 

Reply to Water & Gas 16mm/sq in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
978

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top