please see the attached diagram.

This is a weird one and I am thinking that it is a supply issue. Has anyone seen this before.

The water heater is an instantaneous heater for a basin at 9.5kw and is in the garage. When it is turned on the lights in the house dim for the duration of the water heater being on. (diagram helps to see how garage and house are connected).

I measured the voltage drop as being 242v to 230v when the water heater is turned on. So not enough current ? or something else on the suppliers side ?

I have checked terminals etc and all cables are tight.

The house / garage are semi rural and it is the last house down the lane.

Scan0005.jpg
 
You maybe having a volt drop problem on the phase that is coming into the house.

As the property is the last on in the lane, depending what is also on the phase could be giving you a voltage drop at origin, when the 9.5Kw load is applied.

Also that 6mm is pretty near it's mark for a 9.5Kw load, as i'm assuming it is SWA buried. How far is the run?
 
thanks for the replies.

no loose connections.

the SWA is burried.

the point is that the kitchen lights dim - they are on a house CU circuit and the water heater is on a garage CU circuit.
 
6mm SWA run of 29 meters. I measured the voltage at 242v in the garage dropping to 230v when the water heater is switched on. The lights dim in the house as well as the garage (and they stay dim until the WH is turned off). The house is on it's own CU fed via 6mtrs of 16mm from a switch fuse next to the meter.
 
I just spoke to my Part P scheme technical help and the advice was that I have a supply issue and should contact my DNO (who are likely to not be interested).
I guess I will have to ask them to turn the wick up - or whatever the technical term is...
 
Try doing the voltage change measurements at the switch fuse. This is the last point where the water heater and lights share a supply. It's only the shared cabling that matters as far as one load influencing another is concerned. You should find that the change in voltage when the heater is turned on is much smaller there, but still enough to be noticed. The human eye is very sensitive to small changes in light level.

It would be interesting to know just how small a change in voltage is regarded as a problem by the householder.
 
Table 4D4A refers:
Max rating of 6mm/3 SWA buried is 38A. 9.5kW @ 240V = 39A, 9.5kW @ 230V = 41A (depends on what voltage the manufacturer is using to claim 9.5kW).
Voltage drop is 6.9mV/A/m = 6.9 x 39 x 29 /1000 = 7.6V volts lost at full load (remembering that it will be more than this in practice as the current is greater than the max tabulated value for the cable anyway).

(if someone wants to do the FULL calculation then feel free, but I'm still only on my first coffee....)

So, irrespective of what's going on at the supply end, it's not a great install to the garage.

Now, if the property is at the end of the chain, is old-ish and relatively small then it could easily be the case that when the DNO put the supply in they reckoned on a max demand of only 50-60A and cabled accordingly. Therefore, ANY sudden large current draw has the same implication to the supply cable - we know already that we get at least a 7v drop just on that one circuit alone. The reason it appears to the eye just on one lighting circuit is simple - your fridge/freezer/TV/hairdryer are capable of still working without telling you, whereas as others have said, the eye will notice the tiniest flicker of light.

I'm out in the sticks in Somerset and it's very common in a large number of properties to see the lights in a kitchen 'twitch' when you turn on the kettle, and it's nothing whatsoever to do with the internal installation.
 
Max rating of 6mm/3 SWA buried is 38A. 9.5kW @ 240V = 39A,

That is for 3 Ph, normally the earthing conductor will not be carrying current (third conductor), I make it 46 A from the table on single Phase.

On my second coffee :ack2:
 
Last edited:

Reply to Water heater causes lights to dim in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
988
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top