Where you see the difference is something like a garage feed (again!) when you might have a planned load of, say, 20A and select a cable to match, then the garage CU has a 20A MCB that provides the overload protection. But the feed for the cable might be a 40A or more fuse that will clear in under 5s on a short but is not offering overload protection for the 20A-rated cable.
This would not comply as the load is not fixed in this case.
A better example would be a feed to a motor starter where the overload protection is incorporated in the starter.