Where you see the difference is something like a garage feed (again!) when you might have a planned load of, say, 20A and select a cable to match, then the garage CU has a 20A MCB that provides the overload protection. But the feed for the cable might be a 40A or more fuse that will clear in under 5s on a short but is not offering overload protection for the 20A-rated cable.

This would not comply as the load is not fixed in this case.

A better example would be a feed to a motor starter where the overload protection is incorporated in the starter.
 
A better example would be a feed to a motor starter where the overload protection is incorporated in the starter.
In an industrial setup that would be the classic example for sure: the feed OCPD is simply for hard faults and there is another system (i.e. the motor starter) that is engineered to have the appropriate time/current characteristics needed to protect the motor against overload in operation.
 
For a heater the distinction is probably academic, if you have a load taking X amps then you size your cable for that and fit a MCB at the matching level. So it would be unusual for the OCPD not to also provide overload protection.
I have seen a j box in a 32A ring forming a spur, serving only an a 3kW immersion with only a 20A switch between the immersion heater and j box. Well it had a flash neon light on it to make it look better. No over-current protection whatsoever except the 32A mcb at the main CU. A 3kW immersion's current draw is not constant as it depends on the voltage, which may fluctuate during day for various reason.
 
Hopefully the mods will find a can of this soon
Someone disagrees with you so they are a troll eh. I noticed you trolled all around my posts - that was not coincidence. When you posted it says, to cut it short, only post relating to the topic, otherwise do not. Take note.
 
Last edited:
Someone disagrees with you so they are a troll eh. I noticed you trolled all around my posts - that was not coincidence. When you posted it says, to cut it short, only post relating to the topic, otherwise do not. Take note.

Did I say you were a troll? I dont think I did, I just made a comment suggesting that there is a troll on the forum and you made an assumption that I was talking about you.

I haven't 'trolled all around your posts' I have replied to new threads or threads I have previously replied to that I feel I can have some input on.
Please don't flatter yourself that I'm following you around!

Yes I disagree with some things you have said and have tried to explain why or put my pount across along with the logic behind it.
 

Reply to Water heater in the Central Heating Systems area at ElectriciansForums.net

Similar threads

glad it was such a simple fix..... And good job the previous owners didnt take it with them
Replies
6
Views
636
  • Question
Thanks mate, not something I have a lot of experience in. But that makes perfect sense
Replies
4
Views
622

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top