When I turn water heater on lights flicker the mcb makes a buzzing noise the mcb is 40a but the heater is 11kw so it should be on a 50 also the service head fuse is 60a so this needs to be upgraded in my opinion.
 
Yeah
 

Attachments

  • [ElectriciansForums.net] Water heater
    Screenshot_20201007-174805_Chrome.jpg
    55 KB · Views: 28
The question to ask is not "Should the MCB be 50A?" but rather "Is the installed cable rated for 50A?"

What size of cable, and how is it routed? (i.e. the "method" that is used to determine the current rating of a given cable size based on its thermal insulation environment).
 
The question to ask is not "Should the MCB be 50A?" but rather "Is the installed cable rated for 50A?"

What size of cable, and how is it routed? (i.e. the "method" that is used to determine the current rating of a given cable size based on its thermal insulation environment).
Cable is a 6mm so I will have to upgrade that to a 10mm as well
 
It’s there any electrical heating in the property?

With 3/4 of the available supply being used for this water heater, it leaves very little left for everything else.

i Would expect a small dim of lights when this heater is drawing current, also I am not surprised about a bit of circuit breaker hum with 45A going through a 40A breaker..

I think you need to do some proper design work before throwing bigger cables and breakers in.
 
It’s there any electrical heating in the property?

With 3/4 of the available supply being used for this water heater, it leaves very little left for everything else.

i Would expect a small dim of lights when this heater is drawing current, also I am not surprised about a bit of circuit breaker hum with 45A going through a 40A breaker..

I think you need to do some proper design work before throwing bigger cables and breakers in.
I have done calculations for all the circuits like i said service head is on a 60 so i need to change this for a 100amp and upgrade the tails
 
like i said service head is on a 60 so i need to change this for a 100amp and upgrade the tails

If this is in the U.K then you need to apply to the local DNO to have the service upgraded.
This may require them upgrading their service cable and also upgrading the local network.
There may be costs involved.

It cannot be assumed that there is spare capacity in the local network.
 
If this is in the U.K then you need to apply to the local DNO to have the service upgraded.
This may require them upgrading their service cable and also upgrading the local network.
There may be costs involved.

It cannot be assumed that there is spare capacity in the local network.
Sorry forgot to say the service head is 100a and 25mm tails there is a fused isolator that is on 60a that i need to upgrade along with the tails coming out of this.
 
When I turn water heater on lights flicker the mcb makes a buzzing noise the mcb is 40a but the heater is 11kw so it should be on a 50 also the service head fuse is 60a so this needs to be upgraded in my opinion.
Lights flickering is down to Voltage Drop VD on a poorly designed installation.

Buzzing is down to the OCPD circuit breaker on/ ot near its tripping limit again to a poorly designed installation
 

Reply to Water heater in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
904
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thank you for the suggestion!
Replies
3
Views
465
Whatever... I awoke this morning ready for an intersting and relaxed day at work at my local branch of the Men's Shed charity. " jobs pending...
    • Like
Replies
0
Views
193

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top