When I turn water heater on lights flicker the mcb makes a buzzing noise the mcb is 40a but the heater is 11kw so it should be on a 50 also the service head fuse is 60a so this needs to be upgraded in my opinion.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Water heater in the UK Electrical Forum area at ElectriciansForums.net
Cable is a 6mm so I will have to upgrade that to a 10mm as wellThe question to ask is not "Should the MCB be 50A?" but rather "Is the installed cable rated for 50A?"
What size of cable, and how is it routed? (i.e. the "method" that is used to determine the current rating of a given cable size based on its thermal insulation environment).
I have done calculations for all the circuits like i said service head is on a 60 so i need to change this for a 100amp and upgrade the tailsIt’s there any electrical heating in the property?
With 3/4 of the available supply being used for this water heater, it leaves very little left for everything else.
i Would expect a small dim of lights when this heater is drawing current, also I am not surprised about a bit of circuit breaker hum with 45A going through a 40A breaker..
I think you need to do some proper design work before throwing bigger cables and breakers in.
like i said service head is on a 60 so i need to change this for a 100amp and upgrade the tails
Sorry forgot to say the service head is 100a and 25mm tails there is a fused isolator that is on 60a that i need to upgrade along with the tails coming out of this.If this is in the U.K then you need to apply to the local DNO to have the service upgraded.
This may require them upgrading their service cable and also upgrading the local network.
There may be costs involved.
It cannot be assumed that there is spare capacity in the local network.
Lights flickering is down to Voltage Drop VD on a poorly designed installation.When I turn water heater on lights flicker the mcb makes a buzzing noise the mcb is 40a but the heater is 11kw so it should be on a 50 also the service head fuse is 60a so this needs to be upgraded in my opinion.