Whats The Difference Between Watts And Va.
What Does It Mean , Is Watts The Power Consumed And Va The Power Available
In a simplistic view, then yes.
If you want the more technical answer, the VA is purely a product of the Voltage produced by the supply and the current drawn from the supply.
Watts is a product of the voltage dropped accross the resistive element of the load and the current drawn from the supply.
Volts Amps Reactive (VAR) is a product of the voltage dropped accross the reactive elements of the load and the current drawn from the supply.
the difference between these values is the Power Factor (ie Watts / VA)
With a power factor of 1, with a purely resistive load (although in practice all loads have some reactive elements) then Watts would equal VA. A generator rated at 10KVa would supply 8Kw at a power factor of 0.8., and 10Kw at unity power factor
VA is quite often refered to as "apparent power", Watts are "true power" and VAR is "reactive power"